corsasport.co.uk
 

Corsa Sport » Message Board » Off Day » House Day » power to outside


New Topic

New Poll
  Subscribe | Add to Favourites

You are not logged in and may not post or reply to messages. Please log in or create a new account or mail us about fixing an existing one - register@corsasport.co.uk

There are also many more features available when you are logged in such as private messages, buddy list, location services, post search and more.


Author power to outside
WATSON
Member

Registered: 16th Jun 05
Location: Fife, Scotland
User status: Offline
23rd Mar 11 at 14:00   View User's Profile U2U Member Reply With Quote

At the moment we are starting a large summer house build that ill be making into a gym ect..

Id like to get some power out there to run a few lights, small heater and a few large items (sunbed ect)..

Whats the best way of doing this? costs?

build will be at the back of our house with the leccy box been at the very front, i dont like the idea of ripping up floor ect to get wires underground in the house! would this have to be done?

adiohead
Member

Registered: 28th Sep 01
User status: Offline
23rd Mar 11 at 14:08   View User's Profile U2U Member Reply With Quote

found this link:
http://wiki.diyfaq.org.uk/index.php?title=Taking_electricity_outside#Taking_electricity_outside
ash_corsa
Member

Registered: 15th Apr 04
Location: Shrewsbury
User status: Offline
23rd Mar 11 at 22:56   View User's Profile U2U Member Reply With Quote

Will need a new circuit taking from your existing distribution board, run in SWA, Probably 6mm going on what your planning of having in there.
Will have to be RCD protected and the summerhouse will have to have an earth spike in the ground as its detached from the house.

What kind of house is it? Could the cable not be taken around the outside of the house, either buried underground or cleated to the wall?

New circuits are notifiable to LABC so you'll either need a Part P compliant spark to do the work or pay Building Control to come and inspect it.

If your not competent, get a professional in, you can always do some of the donkey work for him like dig the trench for the cable.
CORSA NUT
Member

Registered: 3rd Aug 01
Location: Wirral
User status: Offline
24th Mar 11 at 21:35   View User's Profile U2U Member Reply With Quote

Call an electrician....

The end.
CORSA NUT
Member

Registered: 3rd Aug 01
Location: Wirral
User status: Offline
24th Mar 11 at 21:36   View User's Profile U2U Member Reply With Quote

quote:
Originally posted by ash_corsa
Will need a new circuit taking from your existing distribution board, run in SWA, Probably 6mm going on what your planning of having in there.
Will have to be RCD protected and the summerhouse will have to have an earth spike in the ground as its detached from the house.
What kind of house is it? Could the cable not be taken around the outside of the house, either buried underground or cleated to the wall?

New circuits are notifiable to LABC so you'll either need a Part P compliant spark to do the work or pay Building Control to come and inspect it.

If your not competent, get a professional in, you can always do some of the donkey work for him like dig the trench for the cable.


ash_corsa
Member

Registered: 15th Apr 04
Location: Shrewsbury
User status: Offline
25th Mar 11 at 19:36   View User's Profile U2U Member Reply With Quote

Under the Electricity safety, quality and continuity regulations 2002 you cannot export a suppliers earth to an out building (assuming TNCS)
CORSA NUT
Member

Registered: 3rd Aug 01
Location: Wirral
User status: Offline
29th Mar 11 at 19:48   View User's Profile U2U Member Reply With Quote

Your not exporting it! Just extending it. Just like any sub main or garage DB etc
ash_corsa
Member

Registered: 15th Apr 04
Location: Shrewsbury
User status: Offline
30th Mar 11 at 18:25   View User's Profile U2U Member Reply With Quote

Im only going on what ive read, apparently it applies to all detached garages/out buildings.

I personally wouldn't do it in my own house but just advising on regs.
CORSA NUT
Member

Registered: 3rd Aug 01
Location: Wirral
User status: Offline
30th Mar 11 at 21:22   View User's Profile U2U Member Reply With Quote

I think it means that the main earth terminal should be a certain distance away from the main fuse. Ie you can't just extend the main earth cable away from the intake to any other building?
Gary
Premium Member

Avatar

Registered: 22nd Nov 06
Location: West Yorkshire
User status: Offline
4th Apr 11 at 16:39   View Garage View User's Profile U2U Member Reply With Quote

quote:
Originally posted by ash_corsa
Will need a new circuit taking from your existing distribution board, run in SWA, Probably 6mm going on what your planning of having in there.
Will have to be RCD protected and the summerhouse will have to have an earth spike in the ground as its detached from the house.

What kind of house is it? Could the cable not be taken around the outside of the house, either buried underground or cleated to the wall?

New circuits are notifiable to LABC so you'll either need a Part P compliant spark to do the work or pay Building Control to come and inspect it.

If your not competent, get a professional in, you can always do some of the donkey work for him like dig the trench for the cable.


Part P sparky only needs to test, anyone compentant can install.

By the sounds of what he wants to put on the new supply i'd have thought a small garage board or simelar mounted at the other end of the building. Unless thats what you meant by 'a new circuit'
Rob_Quads
Member

Registered: 29th Mar 01
Location: southampton
User status: Offline
4th Apr 11 at 18:23   View User's Profile U2U Member Reply With Quote

quote:
Originally posted by Gary

Part P sparky only needs to test, anyone compentant can install.

By the sounds of what he wants to put on the new supply i'd have thought a small garage board or simelar mounted at the other end of the building. Unless thats what you meant by 'a new circuit'


Part P Sparky is only allowed to certify his own work.

The only person that can certify someone elses work is someone appointed by the building control after you give them building notice. This must be done BEFORE starting the work.

If you do work yourself and don't tell the LABC then your screwed as there is currently no post approval like there is with planning permission etc. All you can then do is get a PIR done but this is more of a general check than one specific to the work you have done.
ash_corsa
Member

Registered: 15th Apr 04
Location: Shrewsbury
User status: Offline
4th Apr 11 at 20:56   View User's Profile U2U Member Reply With Quote

quote:
Originally posted by Gary
Part P sparky only needs to test, anyone compentant can install.

By the sounds of what he wants to put on the new supply i'd have thought a small garage board or simelar mounted at the other end of the building. Unless thats what you meant by 'a new circuit'


You would be installing a new distribution circuit. Besides, any outdoor electrical work is notifiable and Rob is right in saying a part P spark will only sign off their own work.
Gary
Premium Member

Avatar

Registered: 22nd Nov 06
Location: West Yorkshire
User status: Offline
4th Apr 11 at 20:59   View Garage View User's Profile U2U Member Reply With Quote

Part P won't or can't?

As far as I've always known a tester can test someone elses work.
17th ed states any 'competent person' can install so
Rob_Quads
Member

Registered: 29th Mar 01
Location: southampton
User status: Offline
5th Apr 11 at 09:15   View User's Profile U2U Member Reply With Quote

quote:
Originally posted by Gary
Part P won't or can't?

As far as I've always known a tester can test someone elses work.
17th ed states any 'competent person' can install so


Correct they can test someone elses work but all they could issue is a PIR. If they issue a full certificate then they are breaking the rules. Obviously if they want to break the rules thats up to them but they would be liable if anything happened due to the work you had done.



[Edited on 05-04-2011 by Rob_Quads]
Gary
Premium Member

Avatar

Registered: 22nd Nov 06
Location: West Yorkshire
User status: Offline
5th Apr 11 at 11:28   View Garage View User's Profile U2U Member Reply With Quote

Fair enough, Whats a PIR?
Rob_Quads
Member

Registered: 29th Mar 01
Location: southampton
User status: Offline
5th Apr 11 at 14:29   View User's Profile U2U Member Reply With Quote

Periodic Inspection Reports (PIR)
Gary
Premium Member

Avatar

Registered: 22nd Nov 06
Location: West Yorkshire
User status: Offline
5th Apr 11 at 19:35   View Garage View User's Profile U2U Member Reply With Quote

So why does 17th say anyone can install if no one can legally test it?
Rob_Quads
Member

Registered: 29th Mar 01
Location: southampton
User status: Offline
6th Apr 11 at 15:22   View User's Profile U2U Member Reply With Quote

You can legally get it tested but it must be done by someone appointed by the council. You must first submit buildings notice to say your going to make changes.

Whether you do it yourself or an electrician does it, it needs to be to code. If they are certified they can sign the work off otherwise it has to be done by a buildings council nominated electrician.
Gary
Premium Member

Avatar

Registered: 22nd Nov 06
Location: West Yorkshire
User status: Offline
6th Apr 11 at 19:14   View Garage View User's Profile U2U Member Reply With Quote

Fair enough. Learn something new every day!

Bit stupid that you've gotta tell building control before you rewire something!
ash_corsa
Member

Registered: 15th Apr 04
Location: Shrewsbury
User status: Offline
6th Apr 11 at 21:07   View User's Profile U2U Member Reply With Quote

quote:
Originally posted by Gary
As far as I've always known a tester can test someone elses work.
17th ed states any 'competent person' can install so


A competent person isn't someone who thinks they know what they're doing, you need sufficient training, experience and qualifications to be recognised as a 'competent person'in the industry.




[Edited on 06-04-2011 by ash_corsa]

 
New Topic

New Poll

  Related Threads Author Forum Replies Views Last Post
POWER?????? ninjauk Help Zone, Modification and ICE Advice 8 1533
7th Mar 04 at 10:42
by neophyterulez
 
whic would be faster? Dave A General Chat 154 5423
21st Jan 12 at 02:15
by stan_the_man
 
Corsa B power steering set up for xe, liquid neo2 Parts Offered 17 1710
28th Dec 07 at 22:38
by neo2
 
Hard Drive Standards - IDE/SATA Ian Geek Day 11 1007
26th Nov 07 at 12:29
by M2RTY
 
600bhp Corsa???? Ryk General Chat 44 3273
7th Feb 08 at 19:34
by Fad
 

Corsa Sport » Message Board » Off Day » House Day » power to outside 28 database queries in 0.0119879 seconds